MCB Breaking Capacities


  • Please log in to reply
15 replies to this topic

#1 OFFLINE   Strima

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 09:21 PM

Heard this back in Jan when our NIC guru turned up.

If you have manufacturers MCB's in the same manufacturers enclosure, for example Hager in Hager, and they have a breaking capacity rating of 10kA then the actual rating can be increased to 16kA.

Before I go running off and quoting someone's word of mouth as gospel has anyone actually seen this in black and white?

I've been told this is now industry standard and would certainly pull us out of the poo on some jobs as the PFC can be a little high at times.

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#2 OFFLINE   RoB Re: MCB Breaking Capacities

RoB

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,194 posts
  • LocationNorth West
  • Skill Areas:Industrial, Control & Automation, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified

Posted 16 February 2013 - 09:28 PM

Haven't heard this, can't see how it changes the durability of the internals of an Mcb dependent of where it's fitted.

Maybe it's due to Warrenty of parts?

Go to work, send your kids to school. Follow fashion, act normal. Walk on the pavement, watch T.V. Save for your old age, obey the law. Repeat after me: I am free


#3 OFFLINE   Spark 68 Re: MCB Breaking Capacities

Spark 68

    EB Senior Member

  • Advanced Members
  • PipPipPip
  • 331 posts
  • LocationUK
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Inspection & Testing
  • Scheme Affiliation:Elecsa

Posted 16 February 2013 - 09:30 PM

It was in annexe Za, I think it was in the 17th red book, but cannot say I have seen it in the BGB.

It was to do with the type testing of the assembly if I recall, and partly due to reduced PFC by the connections, I may be wrong on these points though.

Edited by Spark 68, 16 February 2013 - 09:32 PM.

"In a battle of wits, it is considered poor sport to fight an unarmed man"

"A pat on the back is a foot away from a kick up the Ass"


#4 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 09:30 PM

Could be down to the enclosure and correctly fitted MCB's with spare way blanks etc contains more of the 'blast'?

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#5 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 09:50 PM

Have found this on a forum but my google head isn't working tonight:

The UK has an A deviation to BS 60947 which effectively says that all Customer Distribution Boards used as described above have a conditional prospective fault current rating of 16kA - REGARDLESS of the prospective fault current rating of the individual mcbs or fuses.


There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#6 OFFLINE   Tony Re: MCB Breaking Capacities

Tony

    EB Staff.

  • Global Moderators
  • 5,861 posts
  • LocationResting under the Major Oak
  • Skill Areas:Industrial, Control & Automation, Machinery, Hazardous Area, Teaching
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:MIET

Posted 16 February 2013 - 10:01 PM

Can’t make my mind up on this but I get the feeling they are pushing for the exclusive use of OEM gear in a board. I can’t see how the housing can affect the maximum breaking capacity. Thermal and instantaneous O/L yes……. But?

I’m guilty! Whatever it was, I did it!
I really must start taking my anti-paranoia pills.


Please support the Fatally Flawed campaign.

 

You will take your knowledge to the grave, in the meantime give it freely.


#7 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 10:09 PM

There is mention in the regs of using another back-up protective device on the supply side, 536.1. This allows you use use a lower breaking capaity if required, but still doesn't answer my question...

Why are the regs not so clear cut??? :rolleyes:

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#8 ONLINE   Lenny Re: MCB Breaking Capacities

Lenny

    EB Staff.

  • Administrators
  • 3,688 posts
  • LocationSouth Wales
  • Skill Areas:Commercial, Industrial, Agricultural, Control & Automation, Machinery, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:Eng-Tech, MIET

Posted 16 February 2013 - 10:21 PM

BS60439 Annexe Za.

I have a copy on the PC, I'll put it up when I'm on it next.

There are a few conditions that must be met but essentially all domestic type CUs and MCBs are type tested to 16KA.



#9 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 10:27 PM

Cheers Lenny, I knew someone here would know.

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#10 ONLINE   Lenny Re: MCB Breaking Capacities

Lenny

    EB Staff.

  • Administrators
  • 3,688 posts
  • LocationSouth Wales
  • Skill Areas:Commercial, Industrial, Agricultural, Control & Automation, Machinery, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:Eng-Tech, MIET

Posted 16 February 2013 - 10:34 PM

HERES THE MEAT.........

"These distribution assemblies are for use on AC supplies, with a nominal voltage to earth not exceeding 300V. The outgoing circuits include short circuit protective devices, each having a rated current not exceeding 125A with a total incoming load current not exceeding 250A.
In the UK, such equipment is referred to as a ‘Consumer Unit’ and as such is covered by this Standard. However, additional requirements from annex ZA of the standard call for the assembly to have an additional test; this is known as the ‘conditional withstand test’. The condition is that the consumer unit must withstand a 16kA short circuit fault when protected by a 100A HRC fuse to BS 1361 type II. Further requirements are addressed by this annex:
• Means of isolation to be via a manual double pole switch disconnector
• Rated current of consumer unit is determined by current rating of incoming device.
• Outgoing protective devices can be MCB’s, Fuses and/or RCBO’s.
* No diversity factors are applicable to consumer units, the incoming circuit and the bus-bar system must be able to carry their full rated current without exceeding the temperature rise limits."

#11 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 16 February 2013 - 10:43 PM

Awesome stuff mate, will help us out on the ground. We mainly deal with Hager and some Crabtree thrown in for good measure on the streetworks Telecoms power cabinets. They all have domestic CU's fitted but often the PFC is over 10kA which means running around to try and find an MCB to suit.

We do pre-installation surveys but these are normally carried out by telecoms engineers with little understanding of the magical art so we're often caught out on installation day and the company won't allow us to carry spares due to cost, even though they'll happily spend £90 on Flexicon glands that never get used per job...

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#12 OFFLINE   Johnboy6083 Re: MCB Breaking Capacities

Johnboy6083

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 554 posts
  • LocationSouth East
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Inspection & Testing
  • Training:Completed Apprenticeship

Posted 17 February 2013 - 01:15 PM

This is standard on larger installs, and one reason why some larger DBs have MCCB incomers.
Otherwise, in installs near substations, an MCB wouldn't be suitable for final circuit protection at all.

#13 ONLINE   Lenny Re: MCB Breaking Capacities

Lenny

    EB Staff.

  • Administrators
  • 3,688 posts
  • LocationSouth Wales
  • Skill Areas:Commercial, Industrial, Agricultural, Control & Automation, Machinery, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:Eng-Tech, MIET

Posted 17 February 2013 - 04:30 PM

I've added the full Annexe Za in the download section now.

#14 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 17 February 2013 - 06:16 PM

Cheers mate.

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.


#15 OFFLINE   Spark 68 Re: MCB Breaking Capacities

Spark 68

    EB Senior Member

  • Advanced Members
  • PipPipPip
  • 331 posts
  • LocationUK
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Inspection & Testing
  • Scheme Affiliation:Elecsa

Posted 17 February 2013 - 06:36 PM

This is actually a good reg/annexe to be aware of, I have seen some otherwise top notch sparks fall down on this aspect, especially when carrying out EICR's and giving the wrong coding.

"In a battle of wits, it is considered poor sport to fight an unarmed man"

"A pat on the back is a foot away from a kick up the Ass"


#16 OFFLINE   Strima Re: MCB Breaking Capacities

Strima

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,720 posts
  • LocationSt Neots
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Short Course
  • Scheme Affiliation:NICEIC
  • Professional Registrations:IOSH

Posted 17 February 2013 - 06:40 PM

Very true, I wasn't aware of this until Jan this year and it would have saved us a few problems in the past, not to mention man hours and cost of revisits.

There's only two things I hate in this world. People who are intolerant of other people's cultures and the Dutch.