Volt stick lighting up at gas meter


  • Please log in to reply
12 replies to this topic

#1 ONLINE   oldtimer

oldtimer

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 2,704 posts
  • LocationEdinburgh
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Alarms, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified

Posted 02 February 2014 - 02:55 PM

Guys was called out last week to a 2nd floor flat British Gas was to have moved the gas meter but refused because the fitter checked the gas meter pipework with a volt stick and it lit up. He added that it could be nothing but he could go no further until it was checked out .

 

Had a look it was a split CU one side RCD and non RCC

Supply was a TNCS (Ze=0.06)

Gas pipe bonded with a 10mm

Water pipe bonded by a 10mm

 

I checked this out and measured for voltage at the meter via a separate earth and nothing and yep volt stick lit up I eventually tracked the problem down to the central heating boiler but went no further as it is under a maintenance contract .

 

So I take it this can be common on a TNCS or PME supply in a flat ? Anybody had this and what checks do you do ie amp probe the gas pipework and any faults that you have found causing this

 


Don't have an ego to bruise always learning happy to help but don't tolerate fools gladly

 

Electrician Edinburgh


#2 OFFLINE   Hertz a lot Re: Volt stick lighting up at gas meter

Hertz a lot

    EB Member

  • Tutors
  • PipPip
  • 136 posts
  • LocationLeeds, West Yorkshire
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Machinery, Inspection & Testing, Teaching
  • Training:Completed Apprenticeship, Short Course, Fully Qualified
  • Professional Registrations:IOSH

Posted 02 February 2014 - 04:08 PM

If you have no potential between pipework and earth, then you have no problem. Voltsticks aren't and shouldn't be used for testing as you know. Voltsticks light up for all sorts of reasons, and should be ignored, a calibrated voltmeter is far better. The BG engineer needs some training by the sounds of it, or he should at least leave the electric to someone like yourself who knows what they are doing!

 

Cheers………..Howard


  • JD6400 likes this

http://www.appris.co.uk Check our prices on emagster


#3 OFFLINE   MDJ Re: Volt stick lighting up at gas meter

MDJ

    EB's friendly Ogre

  • Advanced Members
  • PipPipPipPip
  • 1,611 posts
  • LocationGloucester, England
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Alarms, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:ECS/JIB

Posted 02 February 2014 - 05:02 PM

Guys was called out last week to a 2nd floor flat British Gas was to have moved the gas meter but refused because the fitter checked the gas meter pipework with a volt stick and it lit up. He added that it could be nothing but he could go no further until it was checked out .

 

Had a look it was a split CU one side RCD and non RCC

Supply was a TNCS (Ze=0.06)

Gas pipe bonded with a 10mm

Water pipe bonded by a 10mm

 

I checked this out and measured for voltage at the meter via a separate earth and nothing and yep volt stick lit up I eventually tracked the problem down to the central heating boiler but went no further as it is under a maintenance contract .

 

So I take it this can be common on a TNCS or PME supply in a flat ? Anybody had this and what checks do you do ie amp probe the gas pipework and any faults that you have found causing this

Oh no, Oh dear, Gasp


Gloucester, what a place= http://en.wikipedia....wiki/Gloucester


#4 ONLINE   oldtimer Re: Volt stick lighting up at gas meter

oldtimer

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 2,704 posts
  • LocationEdinburgh
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Alarms, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified

Posted 02 February 2014 - 05:30 PM

Agreed and call me cynical but why all of a sudden are the meter guys doing this other to say Ahh Haa you have a major problem and I can get my company to look at it for you christ there was a bloody big 10mm earth cable bonded to the pipe.

 

Plus this is the first time I have heard of this so no doubt I can expect more and I want to be prepared.

 

I had a problem last year where a metal sink was "live" and tracked it down to the washing machine socket earth being adrift and the sink being bonded to the washing machine socket earth terminal with plastic supply pipes so once the earth was reconnected problem was solved


Don't have an ego to bruise always learning happy to help but don't tolerate fools gladly

 

Electrician Edinburgh


#5 ONLINE   oldtimer Re: Volt stick lighting up at gas meter

oldtimer

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 2,704 posts
  • LocationEdinburgh
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Alarms, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified

Posted 02 February 2014 - 05:41 PM

Oh no, Oh dear, Gasp

Care to comment 

 

Is this a new BG wheeze ? the reason I ask is I get called out about 7-10 times a year and its always O my god you have no earth only to find on all of one they do have an earth 


Don't have an ego to bruise always learning happy to help but don't tolerate fools gladly

 

Electrician Edinburgh


#6 OFFLINE   MDJ Re: Volt stick lighting up at gas meter

MDJ

    EB's friendly Ogre

  • Advanced Members
  • PipPipPipPip
  • 1,611 posts
  • LocationGloucester, England
  • Skill Areas:Domestic, Commercial, Industrial, Control & Automation, Alarms, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:ECS/JIB

Posted 02 February 2014 - 06:46 PM

comment about  using a volt stick? I had better not, tony or lenny may ban me. they should be thrown away, appalling items of equipment and only enthusiasts use them ;)



if you do use one then at least use 2 together lol


  • Tony, Geordie Spark, Top Cat and 2 others like this

Gloucester, what a place= http://en.wikipedia....wiki/Gloucester


#7 OFFLINE   Tony Re: Volt stick lighting up at gas meter

Tony

    EB Staff.

  • Global Moderators
  • 8,630 posts
  • LocationResting under the Major Oak
  • Skill Areas:Industrial, Control & Automation, Machinery, Hazardous Area, Teaching
  • Training:Completed Apprenticeship, Fully Qualified
  • Professional Registrations:MIET

Posted 02 February 2014 - 09:56 PM

I'll not ban you. The bloody things should be in the bin! I'll help any way I can to hurt GB


I’m guilty! Whatever it was, I did it!
I really must start taking my anti-paranoia pills.


Please support the Fatally Flawed campaign.

 

You will take your knowledge to the grave, in the meantime give it freely.


#8 OFFLINE   Davethsparky Re: Volt stick lighting up at gas meter

Davethsparky

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,744 posts
  • LocationSurrey
  • Skill Areas:Domestic, Commercial, Agricultural, Inspection & Testing
  • Training:Completed Apprenticeship, Fully Qualified

Posted 02 February 2014 - 10:24 PM

There's nothing wrong with volt- sticks as long as you remember the golden rule-

 

If it lights up red it's probably live and if it doesn't light up its probably live.


  • Geordie Spark, Top Cat, JD6400 and 6 others like this

#9 OFFLINE   Glospark Re: Volt stick lighting up at gas meter

Glospark

    EB Senior Member

  • Advanced Members
  • PipPipPip
  • 360 posts
  • LocationGlossop, Derbyshire
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Scheme Affiliation:Elecsa

Posted 14 March 2015 - 11:01 AM

Just had a call this morning from a customer saying that National Grid were installing new feed and would connect to his meter because the meter was and internal pipework was live.

 

No surprise that when I had put my voltmeter between MET and meter we had 0 volts. Got them out of the van before leaving and asked their hole digger to test again and lit up, then nothing then lit up etc etc. He even went out to his van, got a brand new volt stick, tried it and didn't light.

 

All bonding in place and Ze check and left. Even better is that Nation Grid are reimbersing the customer for my time, so price suddendly increased!


  • durhamsparky likes this

#10 OFFLINE   Dcf Re: Volt stick lighting up at gas meter

Dcf

    EB Respected Member

  • Members
  • PipPipPipPip
  • 564 posts

Posted 14 March 2015 - 02:03 PM

I had this last year when the gas mains were being replaced.
Volt stick lights up at 10mm to gas pipe.
0 volts from met to gas bond of course.
Turn main switch off it disappears.
I couldn't get any volts on the gas pipe to earth bonded or unbonded.
Just about as good as the gas board" engineers" who left a customer of mine with no hot water for a week as they had to order a side entry immersion.
Only for it not to be the immersion at all but the timer!
And then to cap it off bg electrician says he can't touch the controls and left.
They really do boil my pish

#11 OFFLINE   ferg Re: Volt stick lighting up at gas meter

ferg

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,559 posts
  • LocationN.W. Scotland
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Completed Apprenticeship, Short Course

Posted 15 March 2015 - 10:11 AM

I think they have their uses albeit very limited.

 

I used to use one but since I lost it a couple of years ago I haven't replaced it and TBH don't miss it.

 

I only get annoyed when seeing people using them as a primary tool.

 

I.E. (Not so) safe isolation. only fault finding tool etc.

 

The only culprits of this I've come across are plumbers, builders, handymen etc.



#12 OFFLINE   durhamsparky Re: Volt stick lighting up at gas meter

durhamsparky

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,619 posts
  • LocationPit Yaker Land
  • Skill Areas:Domestic, Commercial, Industrial, Agricultural, Alarms, Inspection & Testing, Teaching
  • Training:Completed Apprenticeship, Short Course, Fully Qualified
  • Scheme Affiliation:Elecsa

Posted 15 March 2015 - 10:19 AM

my volt stick would glow red when put against the cat!!

 

ive since bonded the cat to the radiator, although next week i may myself be getting bonded in jail by a big black guy as the RSPCA are prosecuting me!


  • Tony, Top Cat and ferg like this

_____________________________________________________________________________________________________

Steveo

TMIET
EngMonkeyTech

Wife Ignorer
Part Time Clown

 


#13 OFFLINE   ferg Re: Volt stick lighting up at gas meter

ferg

    EB Respected Member

  • Advanced Members
  • PipPipPipPip
  • 1,559 posts
  • LocationN.W. Scotland
  • Skill Areas:Domestic, Commercial, Inspection & Testing
  • Training:Completed Apprenticeship, Short Course

Posted 15 March 2015 - 11:27 AM

My appropriately named Metrel handyman voltstick used to light up when I put it in my pocket.

 

Must have been my electric personality.

 

Or alternatively it was crap and picked up the static.